Please help ASAP on Atwood Furnace

So I Have a 2007 trailer and I am having issues with my furnace. It worked great a week ago now all the sudden it doesn't.

The fan turns on and the furnace will light but then it will shut down. Does it 3 times then will shut itself off eventually. I don't see any codes. It already has the dinosaur board in it. As it lights the little bulb turns red but when it shuts off its green. For the little amount of time the flame runs it still sounds like its clicking trying to start. Atwood told me to replace the electrode which is also the flame sensing and I did. Still same problem. I have seen tons of forums of people with the same issue but rarely a solution is posted. Any help on this thing? Im in desperate need guys I hope you can help. Thanks so much in advance.

model : atwood 8531-IV-DCLP
  • yep, regulator at tanks. Only 13 months old too. Just out of warranty.
  • so the same thing was happening to you even though the stove and refer was working fine? The gas regulator up by the propane tanks or in the furnace?
  • Same thing happened to me recently.
    The propane regulator wasn't supplying enough gas pressure.
    Replaced with a Marshall and all is well now
  • I will try that when I get home today. Any other ideas guys?
  • Close the valves on your propane tanks, remove the hoses. Reconnect everything, now open the valves very slowly. Most likely, you tripped to OPD ( Overflow Protection Device ) from opening to quickly.
  • BURNER FAILS TO IGNITE AND BLOWER FAILS TO RUN

    --------------------------------------------------------------------------------

    CONDITION
    SOLUTION


    1)No electrical power to the furnace
    2)Thermostat defective
    3)Thermostat wires broken or shorted
    4)Current overload protector device defective or
    tripped (circuit breaker)
    5)Blower relay defective
    6)Wire off motor
    7)Wire off relay
    8)Improper ground
    9)Blower motor defective

    1a)Reconnect or replace power source*
    2a)Replace thermostat
    3a)Replace wire or wires*
    4a)Reset circuit breaker
    Check amp draw from motor according to furnace's specification
    5A)Replace relay
    6a)Reconnect wire
    7a)Reconnect wire
    8a)Clean and secure grounds*
    9a)Replace motor



    BLOWER RUNS BUT FAILS TO IGNITE

    --------------------------------------------------------------------------------

    CONDITION
    SOLUTION


    1)Low voltage
    2)Gas pressure incorrect

    3)Furnace grounding wires not secure
    4)Air intake restricted
    5)12 volt polarity reversed
    6)Motor running slow

    7)Exhaust blocked
    8)Combustion air wheel loose
    9)Sail switch defective or wire off
    10)Limit switch defective or off wire
    11)Edge connector on cicuit board dirty
    12)Circuit board defective
    13)
    Gas valve defective

    14)Main burner orifice blocked
    15)High tension lead wire defective
    16)Electrode out of adjustment
    17)Electrode defective
    18)Obstructed burner head

    1a)Correct Power Supply*
    2a)Set pressure to a minimum of 11"W.C. with all appliances running. (Replace regulator if not obtainable).*
    3a)Clean and secure grounds established*
    4a)Clean air intake*
    5a)Correct polarity*
    6a)Check voltage first
    If 12 VDC while running, replace motor
    7a)Clean exhaust*
    8a)Reposition and tighten
    9aReconnect wire or replace
    10aReconnect wire or replace
    11a)Clean with pencil eraser
    12a)Clean plug contacts. If still defective, replace. (check on board tester when possible).
    13a)Replace valve or valve coil, depending on problem encountered
    14a)Clean main burner orifice or replace
    15a)Replace wire
    16a)Adjust electrode (take care not to damage porcelain)
    17a)Replace
    18a)Clean burner head*



    BURNER IGNITES BUT IGNITION SYSTEM "LOCKS OUT" AND TURNS BURNER OFF

    --------------------------------------------------------------------------------

    CONDITION
    SOLUTION


    Low gas pressure

    Exhuast blocked
    Combustion air wheel loose
    Electrodes out of adjustment
    Electrode defective
    Circuit board defective

    Flame sensor wire between electrode and
    circuit board defective
    Air leakage at gaskets
    Defective heat exchanger

    Set pressure to a minimum of 11"W.C. with all appliances running. Replace regulator if not obtainable.*
    Clean Exhaust*
    Reposition wheel and tighten
    Adjust electrode according to furnace specifications
    Replace electrode
    Clean plug contacts. If still defective, replace. (Check on board tester when possible).
    Replace wire

    Replace gasket
    Replace heat exchanger



    SOOTING (caused by lazy yellow flame)

    --------------------------------------------------------------------------------

    CONDITION
    SOLUTION


    Low gas pressure

    Low voltage
    Air leakage at gaskets
    Combustion wheel installed backwards
    Blockage in heating chamber or burner head
    Faulty motor

    *Set pressure to a minimum of 11"W.C. with all appliances running. Replace regulator if not obtainable
    Correct power supply*
    Replace gaskets
    Reposition wheel and tighten
    Clean or replace
    Replace motor



    FAN RUNS CONTINOUSLY WITH THERMOSTAT "OFF"

    --------------------------------------------------------------------------------

    CONDITION
    SOLUTION


    Defective thermostat
    Shorted thermostat leads
    Defective relay

    Replace thermostat
    *Replace wire or wires.
    Replace relay



    LIMITING = BURNER CYCLING ON AND OFF
    BLOWER RUNS CONSTANTLY WITH THERMOSTAT ON

    --------------------------------------------------------------------------------

    CONDITION
    SOLUTION


    Furnace over fired

    Restricted return air supply

    Restricted or insufficient discharge ducting

    Defective limit switch

    Set gas pressure to a minimum of 11"W.C. with all appliances running. Replace regulator if not obtainable. Also, check main burner orifice, it must comply with furnace's specifications.*
    Make sure return air meets furnace's minimum requirements.*

    a. Ducting must meet furnace's minimum requirements*
    b. No excess ducting or unnecessary bends*
    c. All closeable registers must be fully open and unrestricted*
    Replace limit switch



    BLOWER SHUTS OFF AT SAME TIME BURNER SHUTS OFF

    --------------------------------------------------------------------------------

    CONDITION
    SOLUTION


    Wired wrong
    Faulty relay

    Correct wiring*
    Replace relay



    BLOWER VIBRATES OR IS NOISY

    --------------------------------------------------------------------------------

    CONDITION
    SOLUTION


    Motor mount loose

    Damaged blower wheel
    Motor shaft bent

    Tighten motor mounting bracket
    a. Ducting must meet furnace's minimum requirements* b. No excess ducting or unecessary bends* c. All closable registers must be fully open and unrestricted
    Replace blower wheel
    Replace blower motor



    INSUFFICIENT HEAT

    --------------------------------------------------------------------------------

    CONDITION
    SOLUTION


    Furnace under fired

    1. Set gas pressure to 11"W.C. with all appliances running. Replace regulator if not obtainable. Also, check main burner orifice, it must comply with furnace's specifications*
    2. Check ducting and return air according to furnaces specifications*