lostnconfused wrote:
Its in my garage, the main breaker is a 100amp. All the breakers in the box are two pole?
Did you connect the white and black wires to the two poles of that double breaker?
THAT is 240 volts and is going to cost you - big time!
You SHOULD have had a single pole 30A breaker and connected the white wire to the neutral bus.
THEN you mixed up the green and white:S
I suspect your electrical knowledge is minimal!!
Strongly recommend you get an electrician to sort it out BEFORE you replace all the 110 volt appliances in the rig.
You might want to talk to your insurance company. IF they cover it, the bill could be many hundreds, even thousands!
I apologize if this is not a warm welcome for a new member, but I suspect you screwed up BIG TIME and could have killed someone!