Weak breakers will trip when at or near full capacity. Replacing it with a 30A breaker is dangerous. You then have no protection of the undersized wiring with the resulting possability of fire. 20A is really borderline for a AC unit, especially if it a 15K AC unit. Replace the breaker with the same size then refrain from using the AC on 20A.