roof A/C TRIPS 20 AMP BREAKER

WORKING ON ROOF A/C it runs and is cold for about 15 to 20 minutes and then it trips the 20amp breaker that it is connected to. trailer breaker box. I was thinking possibly I should use a 30 amp breaker. Do you have any suggestions

13 Replies

  • Low voltage will cause the AC to draw more current, what size power cord are you using to feed it and how long is it?

    Next I would see what the current draw rating is on the AC unit.

    If you up the circuit breaker to 30 amps you may be pulling 30 amps through wires that are only rated for 20 amps. Not a good idea.
  • Weak breakers will trip when at or near full capacity. Replacing it with a 30A breaker is dangerous. You then have no protection of the undersized wiring with the resulting possability of fire. 20A is really borderline for a AC unit, especially if it a 15K AC unit. Replace the breaker with the same size then refrain from using the AC on 20A.
  • Could be a weak breaker. The head pressure may be high. Is the inlet filter clean?