No, a properly wired 50 amp is 120/240 four wire.
Problem with two legs of the same 120 leg can overload your neutral.
RV receptacles are tow opposing legs off the electrical service rated at 50 amps each.
They are wired the same as a standard 4 wire range receptacle.
If yours has the old cartridge and Edison style screw in fuses, you should add a separate small breaker box wired off the main lugs.
Problem with two legs of the same 120 leg can overload your neutral.
RV receptacles are tow opposing legs off the electrical service rated at 50 amps each.
They are wired the same as a standard 4 wire range receptacle.
If yours has the old cartridge and Edison style screw in fuses, you should add a separate small breaker box wired off the main lugs.