theoldwizard1 wrote:Thanks for the update.CA Traveler wrote:
It's OK. RVs don't bond utility power ground and neutral. That's done at the main panel and in your case the barn. The ground is a safety wire and bonding at the barn is consider safe.
WAS considered safe !
This was common practice until about 10 years ago (?) when the National Electric Code (NEC) changed and there can only be on bond in a system and it must be at the first disconnect. After that, 4 wires must be run to each distribution/breaker panel.