Plumber101010 wrote:
1) Does having an a 30 amp plug limit me and I am losing 20 A with the converter?
It is not the plug that will limit you. It is the breaker on the generator that will trip if you try to draw more than 30A.
Plumber101010 wrote:
2) Is there a way to simply remove the plug on the generator and change it to a 50 amp plug and will I gain anything by doing that
Don't remove the receptacle of the generator. Buy an adapter or have an electrician make one for you.
If your trailer is wired with a 50A plug, you likely have 2 air conditioner. I don't that generator will run both.