13.5 rear AC amps

Ramair
Explorer
Explorer
I believe that my rear Dometic 13.5 ac is out of Freon. Everything was working great until a fan blade broke and cut into the condenser fins. Replaced the fan and all is working but not blowing cold air. When running fan only all is working but when switching to cool (ac) I hear the compressor kick in but not blowing cold air. Called dealer and was advised to check the amp draw of the compressor. I know when all is good its should pull 12.5 amps, what would it pull if it was out of Freon. Any help would be greatly appreciated.
Andrew & Donna Reyes
2012 Georgetown 378 XL
23 REPLIES 23

CA_Traveler
Explorer III
Explorer III
Todays A/C power measurements:

Outside temp 75F, utility power

Dometic Penguin 13,500 BTU specs 12.4A compressor, 3.5A fan 120V, 20A CB recommended.

Measure power with PI HW50C which does not display tenths and is located next to the ATS before the CB panel ie There will be additional voltage drop at the A/C input.

A/C with fan 115V 14A, fan only on high 4A.

This suggests to me that for my A/C the specs are reasonably close.

I know from past experience that the HW50C is reasonably close considering that it doesnโ€™t display tenths.

The specs included locked rotor amps but not start up surge amps.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

CA_Traveler
Explorer III
Explorer III
I didn't measure the motor RPM only volts and amps.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

Kayteg1
Explorer II
Explorer II
CA Traveler wrote:
For a motor to deliver a set HP with lower voltage it has to draw more amps.

But why ASSUME a RV A/C works that way??? Indeed my A/C tests years ago showed that the amps decreased with decreased voltage which leads to a vary obvious conclusion: The A/C was producing less cooling and/or air movement.


So you are saying that with lower voltage the motor speed drops?
Could be, although I was under impression that inductive motors regulate rpm by Hz and electric motors are rated at 110V for a reason.
When I have more time I try to use the meter Watts scale and play with different resistance extensions to compare.
Still the main fact is that ACs draw way less amp than they are rated by the factory.

CA_Traveler
Explorer III
Explorer III
Kill A Watt comments: It is an inexpensive and useful device to gain ballpark estimates of power consumption.

Measuring AC power for motors is definitely more involved (than resistive loads) as power factor comes into the picture. Plus the waveform itself may not be a pure sine wave.

And just for information: The Kill A Watt manual says it measures RMS whatever that means for the device. My Kill A Watt does not even work on my MSW inverter so it is definitely not a RMS device which raised a red flag for me concerning how close it actually measures power. Maybe it is close or reasonably close for a sine wave or near sine wave.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

CA_Traveler
Explorer III
Explorer III
For a motor to deliver a set HP with lower voltage it has to draw more amps.

But why ASSUME a RV A/C works that way??? Indeed my A/C tests years ago showed that the amps decreased with decreased voltage which leads to a vary obvious conclusion: The A/C was producing less cooling and/or air movement.

I've never seen mfg specs that show A/C power consumption for varying voltage and temperature. Anyone have a link?

BUT my post was made to suggest that just measuring amps leaves out an important component namely voltage. And using an extension cord with a 10A CB suggests it's small and could have significant voltage drop.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

Kayteg1
Explorer II
Explorer II
usersmanual wrote:
how can anyone go by the factory suggested amp draws?

You will find people with narrow minds everywhere, that is why factory plays it safe and overrate the draw.
Theory and real life are seldom equal.

usersmanual
Explorer
Explorer
Kayteg1 wrote:
At start up electric motors do have to fight kinetic energy, higher friction, thicker oils and less efficiency.
That is why starting amps under the load is several times higher than running amp. If you observe air compressors - they have pressure relieve system that allows the motor to start with no pressure load and then build it gradually.
AC systems do have time delay that will not allow restart till pressure drops down. '
Starting compressor motor with pressure in the system is good way to burn it.
Than the law of physics say that if you need to deliver certain energy aka watts, when voltage drops, the amperage has to go up to compensate.
watts = volts x amps

so in answer to my question your saying that a 13.5 AC compressor when only getting(EG) 113 volts it draws higher amperage than if its getting (eg)118 volts? seems odd to me if that's what u claim because then how can anyone go by the factory suggested amp draws?

Kayteg1
Explorer II
Explorer II
At start up electric motors do have to fight kinetic energy, higher friction, thicker oils and less efficiency.
That is why starting amps under the load is several times higher than running amp. If you observe air compressors - they have pressure relieve system that allows the motor to start with no pressure load and then build it gradually.
AC systems do have time delay that will not allow restart till pressure drops down. '
Starting compressor motor with pressure in the system is good way to burn it.
Than the law of physics say that if you need to deliver certain energy aka watts, when voltage drops, the amperage has to go up to compensate.
watts = volts x amps

usersmanual
Explorer
Explorer
Kayteg1 wrote:
I was always under impression that lower voltage = higher amp to compensate for watts. During my test voltage drop to 113V and was consistient with other meters I have.
When I can't calibrate watts on kill-a-watt, the voltage seem to be correct and the internet shows it as a pretty good gauge.

test


to me this post is confusing? Iam not good at this amperage deal at all but If a AC unit draws 13 amps upon startup at 118 volts would it not still daw 13 amps at 113 volts?/

Kayteg1
Explorer II
Explorer II
I was always under impression that lower voltage = higher amp to compensate for watts. During my test voltage drop to 113V and was consistient with other meters I have.
When I can't calibrate watts on kill-a-watt, the voltage seem to be correct and the internet shows it as a pretty good gauge.

test

CA_Traveler
Explorer III
Explorer III
Kayteg1 wrote:
Measurements done with Kill-a-watt.
BTW whole test done with extension cord having 10 amp breaker on it.
I wouldn't trust a Kill A Watt to be very accurate.

The use of an extension cord suggests the voltage could be less than 120V and that could reduce the amp draw. Years ago 2 of us posted lower A/C amps with lower voltage.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

dougrainer
Nomad
Nomad
Kayteg1 wrote:
dougrainer wrote:
Kayteg1 wrote:
My 13500 AC draws 6.9 amp.
The 15k Carrier did draw 8.
The label is always saying much more because of starting current.


What outside temp were those amp draws taken at? There is NO WAY a 13.5 or 15k would draw less than 10 amps(compressor only). For a AC rated at compressor draw of 12.9 amps(average on most) you would have to have outside ambient of 45 degrees to get it down to 7.9 amps. At 45 degrees, why would you need the AC to run. The "label" has nothing to do with actual running amps. According to the Carrier specs, they have NO 13.5 or 15k that draws less than 12.7 amps(compressor only) at 95 degrees. Doug


I did not know outside temperatures play such big role and remember doing the test in the past in mild weather.
So having 92F outside right now, went to the camper to repeat the test.
My AC need 12V for operation, so had to hook up the battery to do test with converter off.
So final measurements, my attic fan takes 2.4amp and even switch shows 2-speed it operates with only 1.
When I turn on AC at full blast after initial peak the total amp were 7.8, meaning 5.4 amp for the compressor.
After few minutes the draw increased and start showing > 9.
Yes, the air is very cool.
Measurements done with Kill-a-watt.
BTW whole test done with extension cord having 10 amp breaker on it.


Sorry again. Your test equipment is not even close. Please state brand and model of AC and I will give you the CORRECT amp readings. Your post shows that if you do NOT know what you are doing and do NOT use the correct test equipment, you have no clue as to what is actually happening. I have 37 years and still active as a RV Technician and have extensive Dometic/RVP training. The reason I keep posting is just as you stated. You had NO clue as the Ambient could affect your readings. It DOES. Doug

Kayteg1
Explorer II
Explorer II
dougrainer wrote:
Kayteg1 wrote:
My 13500 AC draws 6.9 amp.
The 15k Carrier did draw 8.
The label is always saying much more because of starting current.


What outside temp were those amp draws taken at? There is NO WAY a 13.5 or 15k would draw less than 10 amps(compressor only). For a AC rated at compressor draw of 12.9 amps(average on most) you would have to have outside ambient of 45 degrees to get it down to 7.9 amps. At 45 degrees, why would you need the AC to run. The "label" has nothing to do with actual running amps. According to the Carrier specs, they have NO 13.5 or 15k that draws less than 12.7 amps(compressor only) at 95 degrees. Doug


I did not know outside temperatures play such big role and remember doing the test in the past in mild weather.
So having 92F outside right now, went to the camper to repeat the test.
My AC need 12V for operation, so had to hook up the battery to do test with converter off.
So final measurements, my attic fan takes 2.4amp and even switch shows 2-speed it operates with only 1.
When I turn on AC at full blast after initial peak the total amp were 7.8, meaning 5.4 amp for the compressor.
After few minutes the draw increased and start showing > 9.
Yes, the air is very cool.
Measurements done with Kill-a-watt.
BTW whole test done with extension cord having 10 amp breaker on it.

dougrainer
Nomad
Nomad
Sorry, Carrier FAN MOTOR AMPS are at most 2.75 on hi fan. For every 10 degrees BELOW 95 ambient you subtract 1 amp from the compressor draw. So, your Carrier amp draw at 95 degrees would be 13.2 amps at 95 degrees. Less 2.5 fan the compressor would be at 10.7 amps at 95 degrees. AMP draw on RV compressors MUST be Ambient temp compensated for correct diagnosis. Doug