dougrainer wrote:
EMS, not ECM system. IF the compressor is indeed turning ON and then turning OFF, then the capacitor is not the problem. Doug
There are 2 capacitor type devices in these ac units, A starting capacitor and a running capacitor. The compressor can start and run if the run capacitor is open. It will pull high amps and cut off on it's overload, as the compressor overload cools it will repeat that cycle. The capacitors are located in the side panel under the top cover. The larger metal run capacitor can have 2 or 3 terminals, if it has 3, the capacitor is a dual unit that also contains the fan capacitor. They will have marking to identify the size like 25/5 mfd if it's a dual unit, 25 mfd for the compressor and a 5 mfd for the fan. MFD stands for microfarad. If the capacitor has any distortions at all, it's bad. They typically have a arc that takes place inside the shell of the capacitor that produces gas that swells the end where the terminals are and disconnects the terminals internally. a cheap fix that will restore a ac unit to working condition most times.