philandterri wrote:
We have a 2006 Fleetwood Bounder 32W on a ford chassis. Half of our 120 volt power is not working either on shore power or generator. Found only one ground fault breaker near the stove, checked all breakers. What next?
I'm assuming that you have a 50amp coach, so...
If all the obvious quick checks are OK, along with turning the main breaker off and back on, then...
Pull the cover front off the main breaker box.
Use a voltmeter to see if you have 240vac across both the top and bottom of the double pole main and either side to neutral or ground should read 120vac.
If one leg is missing on top, then check the transfer switch, if the connections are tight.
If one leg is missing on the bottom, replace 50amp breaker.
If the transfer sw. is faulty, it would be rare and have to be stuck midway rather in one position or the other.