Sam Spade wrote:David0725 wrote:
the only thing he had on was the A/C
There should not be ANY high draw devices ON when the generator is first started.
And are you saying that the cord going to the trailer is a "normal" household type plug ??
โMay-23-2016 06:16 AM
DrewE wrote:There is your answer
The "110 plug" I assume means a normal 15A plug such as is used for most household devices. The socket for that on the generator would have either a 15 or (more likely) a 20A circuit breaker. The air conditioner alone comes close to that during startup, and the converter and other AC loads in the trailer add to that, so it's not too surprising that the breaker tripped. Your brother was simply trying to use more current than the socket can safely supply.
Note that a standard circuit breaker only responds to current, not to voltage. It's not even connected to both legs of the circuit, so has no way to "see" the voltage being delivered.
130V is a little high, but not really unexpectedly so for a generator with no load. The nominal domestic power supply standards (at the electric meter) are 120/240V +/- 5 percent, which works out to 114 to 126V. In some areas, at least occasional excursions outside this range are not uncommon, and most decently engineered devices are designed to work with at least a +/- 10 percent variation from nominal.
Some generators have some comparatively low-energy noise on their output that might "fool" meters when they're completely unloaded, but basically disappears with even a pretty small load. The meters aren't lying; they just respond to a high impedance noise source since their input impedance is very high. That may or many not be the case for this particular generator.
I'm guessing the generator may have a 120/240V 30A output, probably a twist-lock style. Wiring up an adapter for that which splits it into two 30A RV receptacles (or a single 50A receptacle used with the appropriate adapter) would go a long way towards solving your difficulties.
โMay-23-2016 05:30 AM
David0725 wrote:
the only thing he had on was the A/C
โMay-23-2016 03:24 AM
โMay-22-2016 10:20 PM
โMay-22-2016 09:17 PM
โMay-22-2016 02:39 PM
MrWizard wrote:
sounds like a portable generator ?
what brand what model ?
sounds like the voltage regulation is acting up/not set correctly
130v is a little high but not outside of limits...
MrWizard wrote:
...tripping the breaker is possibly something, surging (load spiking) on the higher voltage
try turning off the converter charging the batteries and make sure the fridge is on propane (manually set to lp)
some times the electric heating element becomes leaky, and will cause a GFI breaker to trip
or turn off ALL circuit breakers in the 129v electric panel
start generator
plug in
turn on only ONE circuit breaker at a time
โMay-22-2016 02:34 PM
โMay-22-2016 12:54 PM
โMay-22-2016 08:04 AM
โMay-22-2016 06:07 AM
DSDP Don wrote:
You don't say what you're trying to power with the generator. You need to make sure that you don't have an electric water heater turned on, battery charger on coach/trailer turned on while trying to power other things.