wa8yxm wrote:
and in all cases.. There is a very slight "power loss" in the cord, this slight difference means that you are more likely to trip the park's 30 amp breaker than the one in your RV. Plus the park's likely has been abused more and may only be a 25 amp now days (or less).
There is a slight power loss in the cord, but it's a voltage drop and not a loss of current. Since circuit breakers are designed to react to current, not to power, the power loss in the cord does not make the pedestal breaker more likely to trip than the RV breaker.
If you have some electrical device that connects across the leads and consumes power between the inlet and the main breaker, such as an EMS unit, the power that it consumes would lead to additional current at the pedestal breaker vs. the RV main breaker. A wire alone doesn't do that.
In actual operation for moderate overloads or near-overloads, most common circuit breakers actually work as thermal devices (they detect current by the heating of an internal bimetallic strip or something similar) and so the breaker that's in the warmer environment and/or more thoroughly enclosed so as to dissipate less heat would be more likely to trip first, all other things being equal.