Cummins12V98 wrote:theoldwizard1 wrote:rhagfo wrote:
Well we built our own with correct ends for 50 amp cable. The cable is 6/4 SOOW electrical cable. It is rubber insulated rather than PVC. Stays flexible even below freezing.
6/4 SOOW cable
There is no need to use SOOW cordage ! It is rated for 600V. SJOOW is rated for 300V. Also rubber insulated.
Depending on the length, you probably only needed 8/4.
My cord is from a temp power box. It's 6/3 & 8/1 for the ground. Mine is "SOW"
While that is true, I got my cable from a fellow forum member for a very good price. That said, I would not step down to a 8 gauge cable as with Cheap heat I draw 20 amps on both legs during winter.
The real killer is that I wasn't sure my 40' cable was going to reach the 30 amp outlet I installed in my daughters garage when we spent last July there. I built a 23' SOOW extension cord, but I easily reached with our 40' cord.