csamayfield55 wrote:
DrewE wrote:
This is not a likely answer at all. Neutral and ground are only tied together (bonded) at the main panel. If neutral and ground are connected together in a device or elsewhere, that is a ground fault and a dangerous situation. No appliance with a standard three-prong 120V cord should have neutral and ground tied together.
If the neutral were open, three prong devices would fail to operate just as much as two prong devices would fail to operate.
Possibly the outlet is loose and the candle warmer's plug isn't making contact while other plugs are shaped or bent slightly differently and are making contact. Possibly other things were plugged into other outlets in the RV. Possibly the GFCI has tripped and the candle warmer outlet is protected by it.
So you have never seen an outlet with an open neutral? Not saying it is safe at all actually not a good plan but it does happen and can
Chris
I have seen outlets (or cords or whatever) with an open neutral. They are, for all practical purposes, dead in as much as nothing plugged into them will work, even if the things have a three prong plug, precisely because the safety ground is not a current return except under fault conditions. They certainly do not exhibit the symptom of "everything except this one device works."