john&bet wrote:I may be wrong but I don't think this is right. I believe a 50 amp plug has 2 neutral's and 2 hot's and a ground both hots are 50 amp. If so than you will only pull 30 amps from each 50 amp lead if your plug just splits to 2 30 amp plugs.
The safety of the idea has not been address yet so let me be the first. You have the potential to overload the neutral of the adapter or the neutral of the recptical or the neutral anywhere up stream of that point. If both 30 amps are loaded to say 24 amps then there is 48 amps on the neutral which will be pushing it and the connections. JMHO.