STANDBY GENERATORS

M_GO_BLUE1
Explorer
Explorer
We are looking to buy a new stick and brick house close to the grand kids and when completed want to equip it with a standby generator...

For those with a standby generator what fuel type do you have? LP? Natural gas?

Also our fifth wheel has an Onan 5500W gas generator built in...can this be used via a transfer switch to run the house if needed? is 5500W big enough to run the whole house?

Thanks for your time...



2005 Chevy Silverado 3500 dually CC/LB Duramax/Allison


2008 Jayco Designer 35RLTS fifth wheel


Onan 5500W Marquis Gold gas generator (HGJAB - 1038D)

68 REPLIES 68

Jarlaxle
Explorer II
Explorer II
Lantley wrote:
SolidAxleDurango wrote:
wa8yxm wrote:
... Sad to think that the power companies have let their lines get so bad that "Thousands without power" is a common occurrence....


The power companies haven't let anything "get so bad"... The lines are what they are. They are above ground. That was the technology available when they were put up.

If they want the improve reliability during ice/wind/rain/etc, the only way to do so is to move the infrastructure underground.

That is a VERY expensive exercise when 98% of the infrastructure is above ground... They can do it, but we have to want it. And for us to want it, we have to pay for it.

It's very simple economics.


Yes however there are cases in my area where the power company has not kept up with pruning trees. They have also reduced staff and rely on subcontractors more. The power lines due require maintenance. In many cases the maintenance has been lacking due to cost cutting measures.


At least in this area, one reason they haven't trimmed trees is because many residents complained when they did!
John and Elizabeth (Liz), with Briza the size XL tabby
St. Bernard Marm, cats Vierna and Maya...RIP. ๐Ÿ˜ž
Current rig:
1992 International Genesis school bus conversion

Lantley
Nomad
Nomad
SolidAxleDurango wrote:
wa8yxm wrote:
... Sad to think that the power companies have let their lines get so bad that "Thousands without power" is a common occurrence....


The power companies haven't let anything "get so bad"... The lines are what they are. They are above ground. That was the technology available when they were put up.

If they want the improve reliability during ice/wind/rain/etc, the only way to do so is to move the infrastructure underground.

That is a VERY expensive exercise when 98% of the infrastructure is above ground... They can do it, but we have to want it. And for us to want it, we have to pay for it.

It's very simple economics.


Yes however there are cases in my area where the power company has not kept up with pruning trees. They have also reduced staff and rely on subcontractors more. The power lines due require maintenance. In many cases the maintenance has been lacking due to cost cutting measures.
19'Duramax w/hips, 2022 Alliance Paradigm 390MP >BD3,r,22" Blackstone
r,RV760 w/BC20,Glow Steps, Enduraplas25,Pedego
BakFlip,RVLock,Prog.50A surge ,Hughes autoformer
Porta Bote 8.0 Nissan, Sailun S637

SolidAxleDurang
Explorer
Explorer
wa8yxm wrote:
... Sad to think that the power companies have let their lines get so bad that "Thousands without power" is a common occurrence....


The power companies haven't let anything "get so bad"... The lines are what they are. They are above ground. That was the technology available when they were put up.

If they want the improve reliability during ice/wind/rain/etc, the only way to do so is to move the infrastructure underground.

That is a VERY expensive exercise when 98% of the infrastructure is above ground... They can do it, but we have to want it. And for us to want it, we have to pay for it.

It's very simple economics.
TV = 15 Ram 3500 Dually 6.7 / CC-LB / CTD / Aisin / 3.42 / 4wd / EBrake
5er = 12 Keystone Avalanche 330RE
Toys = 08 Kawasaki Brutie Force 650i 4x4 ( x2 ๐Ÿ™‚ ) 14 Arctic Cat Wildcat 1000

wa8yxm
Explorer III
Explorer III
I know a lot of folks who are going to propane fired Genracs and such as a back up to the mains.. Sad to think that the power companies have let their lines get so bad that "Thousands without power" is a common occurrence. I grew up out in the boonies as it were (Story time: Went to buy propane, woman really wanted to give me directions to the tank farm.. She was sure I could not find it, Till I told her my name,,, It is the dairy farm I grew up on). I moved to the city I expected more reliable power.. Well on the farm, we occasionally lost power for a few hours, but I think one time we could not milk the cows with the power milker.

In the city,, Days without power is common.

This is why the first MOD I made to the motor home was so it could feed power to the house, which was also modified (Added proper generator transfer panel and inlet) so the motor home could feed it.

The box, wires, plugs, sockets and installation, Couple thousand dollars.

Click: Furnace comes on,

Warm wife... Priceless.
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times

sh410
Explorer
Explorer
@M GO BLUE

We also have a 1100sq. ft. home. LP powers the range, water heater, and forced air furnace. In the past we powered the lights, TV and well pump with a open frame 3500W generator.

Two months ago we installed a 8kw Generac Guardian standby generator with a auto transfer switch to power a sub panel that includes all of the circuits we wanted to run for including washer and dryer. We often have power outages, some up to 5 days. It has worked twice since installed and performed as expected.

We chose LP because we already have it available with a 1000G buried tank.

NG would be a good choice, however, if you wish to be self reliant, LP would be my choice because the supply is at your residence and would not be dependant on an interuptable source of fuel

Fish__n___Grits
Explorer
Explorer
My 10kw is gasoline, but if it was available, I'd use natural gas. You have to use non-ethanol gasoline, unless you want to buy carburetor kits by the dozen.
Non-ethanol is expensive, too! And you have to consider how to safely store enough to get you through a long outage.
Billy & Dale
'99 F350 DRW Superduty
'02 Lance 1161
Salli the "Schnoodle"

jasult
Explorer
Explorer
I have a Champion 7500 / 9000 and hooked into transfer switch. I bought it with 10 hours use the previous owner picked up from super storm sandy. He could not justify keeping it and I bought it at bargain price
Jim & Georgeanne + Lucie the beagle
"excavator" on the DieselStop.Com
1999 F350 CC LB Hydra chip
1996 F250 Powerstroke, Tony tunes, BTS trans
1995 Fleetwood Wildness 30 ft 5ver

Our Camping Pics and 5ver Album here
Our Gettysburg trip 2010
Williamsburg, Va

legolas
Explorer
Explorer
First a definition - to me whole house means that I can operate off the generator just as though I was still on the grid.

We moved to the Smokies - 30 miles west of Asheville- from Miami. There I had a 15 KW gas powered Generac with manual transfer switch. When I moved here the deciding factor was - cold weather- I did not want to have to go out in 20 degree weather with snow on the ground to start a generator. I have a 350 gal propane tank buried under the rose garden in front of the house and the only thing in the house that uses it is a small backup furnace. So I had a 20 KW Generac with automatic transfer switch installed. Total cost including having the gas company run a line from the tank to the generator was $9,000. The generator has a weekly exercise / test / battery charge cycle, starts up and runs for 12 minutes to do whatever it is that it does. Power goes out - generator comes on in 20 seconds. Power comes back on generator goes off and you don't even know when that happens unless you are close enough to the generator to hear it shut down.

Best $9,000 I ever spent.

wa8yxm
Explorer III
Explorer III
I too have seen power plants using Diesel or Natural Gas generators... one of the cities I have visited in my travels is Page, AZ... This is one city that did not wish to be without power (THink the Y-2K scare)

On one side of town is a hydroelectric dam (Glenn Canyon)
On the other side of town is a coal palnt (Navaho Generating plant)
and in town is a major Internal Combustion plant (Idle less needed, Emergency power)... They put that one in in 1999 just in case.
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times

CavemanCharlie
Explorer III
Explorer III
Hank MI wrote:
CavemanCharlie wrote:
Besides, most of ;but not all; of your electricity is coming from burning fuel. The electric company's must be making money.


Pretty sure they can do it a lot more efficiently than you can using an internal combustion engine.


You may be right. But, I was under the impression that my local electric company generates electricity by using a diesel engine to spin a generator. At one time I know it was by burning coal but, times have changed the big coal piles that were once there are gone, and even the rail road tracks to the site have been removed.

CavemanCharlie
Explorer III
Explorer III
SolidAxleDurango wrote:
john&bet wrote:
Our co-op has some very large users of electricity with standby genset that can power thier whole place and in peak power demand times they are asked to run them to help reduce the load on the system. The agreement is good business since. In fact I helped install a lot of those big kw sets at one such operation.


Asked? No body does anything in business because they are asked. They do things because they are obligated to.

We have some hefty standby generators at work too. Enough capacity to run 400 modern homes. We don't run them for anyone except for us.


Maybe it's not just always because that are obligated but, also because they could save / make money doing such.

SolidAxleDurang
Explorer
Explorer
john&bet wrote:
Our co-op has some very large users of electricity with standby genset that can power thier whole place and in peak power demand times they are asked to run them to help reduce the load on the system. The agreement is good business since. In fact I helped install a lot of those big kw sets at one such operation.


Asked? No body does anything in business because they are asked. They do things because they are obligated to.

We have some hefty standby generators at work too. Enough capacity to run 400 modern homes. We don't run them for anyone except for us.
TV = 15 Ram 3500 Dually 6.7 / CC-LB / CTD / Aisin / 3.42 / 4wd / EBrake
5er = 12 Keystone Avalanche 330RE
Toys = 08 Kawasaki Brutie Force 650i 4x4 ( x2 ๐Ÿ™‚ ) 14 Arctic Cat Wildcat 1000

john_bet
Explorer
Explorer
Our co-op has some very large users of electricity with standby genset that can power thier whole place and in peak power demand times they are asked to run them to help reduce the load on the system. The agreement is good business since. In fact I helped install a lot of those big kw sets at one such operation.
2018 Ram 3500 SRW CC LB 6.7L Cummins Auto 3.42 gears
2018 Grand Design 337RLS

Hank_MI
Explorer
Explorer
CavemanCharlie wrote:
Besides, most of ;but not all; of your electricity is coming from burning fuel. The electric company's must be making money.


Pretty sure they can do it a lot more efficiently than you can using an internal combustion engine.