TXiceman wrote:Tight may not matter if there is corrosion. Need to measure voltage down the line next time you have a cut in power.
It is a 50 amp site with a 50 amp plug only. The two host sites are 50 amp and the rest of the camping loop is 30 amp.
All the trailer connections and connections in the pedestal are tight. The problem has to be prior to the pedestal.
Ken
โFeb-10-2017 06:25 PM
TXiceman wrote:Open or high resistance neutral.
... Without the Auto Transformer, L1 will drop voltage as low as 104 volts which shuts down the EMS. When L1 leg goes low, L2 goes high to about 127 volts with no or a very small load on L2. ...
Reese Dual Cam Straight Line HP Sway Control
โFeb-10-2017 03:38 PM
โFeb-10-2017 12:33 PM
TXiceman wrote:
It is a 50 amp site with a 50 amp plug only. The two host sites are 50 amp and the rest of the camping loop is 30 amp.
All the trailer connections and connections in the pedestal are tight. The problem has to be prior to the pedestal.
โFeb-10-2017 12:03 PM
โFeb-10-2017 11:44 AM
โFeb-10-2017 10:44 AM
โFeb-10-2017 07:33 AM
โFeb-10-2017 06:07 AM
โFeb-10-2017 05:56 AM
โFeb-10-2017 05:14 AM
TXiceman wrote:
Jerry, that is my thinking since they do not know the condition from the flood. They do not have any way to high pot test the wiring. Trying to get the state park to get an electrician out to check it.
Ken
โFeb-10-2017 04:20 AM
โFeb-10-2017 04:00 AM
MrWizard wrote:
do you have true 50amp service
or do you mean you have 30+20 ?
are you on a 30amp with adapter and where is the autoformer in this circuit
30a ped > autoformer > EMS is the correct setup
you can not parallel this with a 20amp on the other leg
total imbalance in the circuits will occur