Qwazert wrote:In fact the amps would be the lower Imp panel.
As I understand things, connecting them in series will not be much of a benefit, since I need more charging CURRENT, as opposed to higher voltage.
โAug-01-2022 07:21 AM
โAug-01-2022 07:15 AM
I have two 12V panels...not a 20.8 and a 22.6...they are both considered as 12V panels.That's Voc (open circuit) which is useful for testing panels. Vmp (maximum power) is used for power along with Imp. Voc and Isc (short circuit) are useful for testing a panel.
โAug-01-2022 05:02 AM
โJul-31-2022 09:44 PM
CA Traveler wrote:
This may help. Solar panel cells are not batteries and are electrically diodes and hence the higher voltage panel cannot backfeed the lower panel. Hence no heating occurs in the lower voltage panel and blocking diodes are not needed. Most modern controller prevent the function of isolating the panels from controller and hence the battery is not discharged at night. Ie Blocking diodes are not needed.
Scroll down the the 4 parallel panel diagram with different amps and voltage for an example. https://solarpanelsvenue.com/mixing-solar-panels/
โJul-31-2022 08:58 PM
โJul-31-2022 08:34 PM
โJul-31-2022 07:40 PM
โJul-31-2022 06:14 PM
Qwazert wrote:You have these panels hooked up AND connected to shore? I guess the simplest answer would be your 2-3 amps is all the batteries are asking for, and adding another panel doesn't make any difference.
Does the controller sense that less is required because the batteries are fully charged (still connected to shore power)?
โJul-31-2022 05:19 PM
โJul-31-2022 05:12 PM
โJul-31-2022 03:29 PM
CA Traveler wrote:time2roll wrote:X2 Your 2 parallel panels can deliver 5.4A+5.17A = 10.57A at 17.6V (the lower voltage panel). This power loss from the higher voltage panel will not be a factor for a PWM controller as long as your wiring losses do not limit the maximum charge rate the battery will accept, ie the absorb voltage for flooded batteries.
Put a 20 amp load on the battery and test again.
โJul-31-2022 02:40 PM
โJul-31-2022 01:30 PM
time2roll wrote:X2 Your 2 parallel panels can deliver 5.4A+5.17A = 10.57A at 17.6V (the lower voltage panel). This power loss from the higher voltage panel will not be a factor for a PWM controller as long as your wiring losses do not limit the maximum charge rate the battery will accept, ie the absorb voltage for flooded batteries.
Put a 20 amp load on the battery and test again.