Ductape wrote:
800 AH you need 160 amp charge current to meet the 20% of capacity recommendation from Lifeline for deep discharge bulk charging. I had a similar setup on our prior coach, and noted some symptoms of early voltage drop under load after a lot of shallow discharges and slow solar recharging.
I had a marine battery selector that allowed me to divide the big bank in half. I found that by halving the bank, drawing the smaller bank down to around 50% and then vigorously recharging with my converter (at 27% of C) they got stronger each cycle. Voltage drop took longer under load and charge acceptance increased.
I also periodically top charge them and use a precision ammeter to ensure I get them to the 1/2% spec.
โMar-05-2018 02:36 PM
BFL13 wrote:
If your AH counter does not take heat loss on recharging into account, then it will over-state the AHs going in and declare you are full when you aren't yet. You will have batteries that are undercharged and sulfating. (as you suspect yours are)
EG Trimetric has a default charging efficiency that is adjustable, but you have to play with that for several recharges to get it right on. So after a while the AH counter gets out of whack and needs to be reset. If you leave it on "auto-reset" and you have solar, it will be wrong by resetting itself every time it gets dark
No idea what the Magnum and Whizbang do about that. However, if you have never reset the AH counter for four years, then it could be reading anything by now.
โMar-05-2018 01:16 PM
โMar-05-2018 01:04 PM
โMar-05-2018 12:42 PM
โMar-05-2018 12:04 PM
โMar-05-2018 10:06 AM
โMar-05-2018 08:48 AM
Smitty77 wrote:
So Gordon - In the boating community, you're saying their's a high probability of these becoming non environmental friendly boat anchors:)!
We come off of this trip mid April, and will limp along as needed.
As I've read here, and elsewhere many times - a non resting battery voltage read is not a true measurement of the batteries voltage. We're moving sites today, but when we get to the new site (Same campground.) I'll make sure the bank is fully charged again. Then we'll turn off all power draw for 3-4 hours, and I'll take a reading at the batteries again.
Question: I'm not disconnecting cables, so these 4 6V's are connected. When I'm taking individual battery readings of interconnected batteries, are they valid or off because they're interconnected? (Really want to see what the 4.15 and 4.5V batteries reading of two days ago, look like after Conditioning cycles.)