Dusty R wrote:
I also don't like those adaptors.
I put 30a RV recital on a 20a circuit where I plug my mh during storage and while loading for our next trip.
Someone once told me that was a code violation, but I don's see a problem with it.
Aug-16-2018 06:33 AM
DrewE wrote:Bobbo wrote:DrewE wrote:
Edit:
I'm also not a big fan of the 30A male to 15A female adapters that are available, partly because I've seen at least one case where one of those adapters, and the reverse 15A male to 30A female, were used with an ordinary (probably 16 gauge?) extension cord to power a 30A RV.
I also don't like those adaptors.
I put 30a RV recital on a 20a circuit where I plug my mh during storage and while loading for our next trip.
Someone once told me that was a code violation, but I don's see a problem with it.
Aug-15-2018 08:28 PM
Bobbo wrote:DrewE wrote:
Edit: Just noticed the 20A outlet there. Is that on the same 30A circuit (without a 15 or 20A breaker protecting it)? If so, that's definitely not up to code and a bit of a concern; the receptacle is underrated for the circuit's ampacity.
My S&B house has a bunch of 15 amp outlets on a 20 amp breaker. The receptacles are undersized for the circuit's ampacity too. As long as the wires going to the 20 amp outlet are sized for 30 amps, I wouldn't loose sleep over it.
Aug-15-2018 07:08 PM
DrewE wrote:
Edit: Just noticed the 20A outlet there. Is that on the same 30A circuit (without a 15 or 20A breaker protecting it)? If so, that's definitely not up to code and a bit of a concern; the receptacle is underrated for the circuit's ampacity.
Aug-15-2018 10:14 AM
DrewE wrote:George3037 wrote:
I just installed a 30A plug for my TT about 3 weeks ago. I used 10 ga. direct burial underground wire inside 3/4" PVC conduit. Ran 50' from post to house and 50' through basement to a 30A breaker in the breaker box in garage. Voltage drop is acceptable.
I measured 121.5 at the breaker and 120.4 at the plug with no load. That's less than the 5% drop I expected.
Measured 119.9 at the trailer end with fridge running, some lights and a TV on. Kicked on the A/C with the above and it measured 113.6V which is about 8% drop under load but acceptable to me.
Total cost was about $450. All materials were bought at HD.
Under no load, the expected voltage drop is zero. (Recall Ohm's law: V = I * R. No load means that the current I is zero, and so the voltage across the resistance--the voltage drop--is also zero.) Maybe the line voltage fluctuated while you were making your measurements, or maybe there was a load you weren't considering such as the converter charging batteries.
At any rate, it seems to be okayish for what you need, so there's no need to speculate on what was going on.
Aug-15-2018 10:07 AM
George3037 wrote:
I just installed a 30A plug for my TT about 3 weeks ago. I used 10 ga. direct burial underground wire inside 3/4" PVC conduit. Ran 50' from post to house and 50' through basement to a 30A breaker in the breaker box in garage. Voltage drop is acceptable.
I measured 121.5 at the breaker and 120.4 at the plug with no load. That's less than the 5% drop I expected.
Measured 119.9 at the trailer end with fridge running, some lights and a TV on. Kicked on the A/C with the above and it measured 113.6V which is about 8% drop under load but acceptable to me.
Total cost was about $450. All materials were bought at HD.
Aug-15-2018 09:37 AM
Boomerweps wrote:
Problem is that it is about 90-100 feet from the home circuit breaker box. Voltage drop calculator has about a 5% voltage drop for that distance using 10awg and about 3.5% using 8awg (not allowing for the TT shore power cord).
I'm thinking I'll need to use 8awg.
Copper gets expensive, plus added components, outside jack, ditchwitch rental, etc.
Any thoughts?
I'm looking at Direct Burial wire or interior grade that would be routed through sealed plastic pipe. I've only checked Home Depot pricing so far and not the local electrical supply house.
Garage has 12awg run to it and is a good 110-120 feet run through the house and ground from the CB box.
Aug-15-2018 08:44 AM
Aug-15-2018 07:37 AM
Aug-15-2018 06:09 AM
valhalla360 wrote:wnjj wrote:valhalla360 wrote:You’ll want communications in a separate conduit above the electrical in the same trench.
Go big on the conduit...as you learned with the old conduit...If you want to run communications or 50amp line later, it's much easier if you have a 2" or even larger conduit to work with and the cost difference is negligible.
It's fine to put comms in the conduit. The only issue is anyone working on it needs to be qualified to work around electricity...assuming you farm out the work.
We did it all the time on signal systems...finally had to change and run independent conduits for power and comms because as we added more high tech devices needing comms, we were getting a lot of technicians who weren't licensed electricians working on the systems, so technically, they were not allowed to go into any part of the system that had live electrical wires. If they were combined, they had to drag an electrician along to watch...by splitting it out, they could go do work by themselves.
Aug-14-2018 10:55 PM
wnjj wrote:valhalla360 wrote:You’ll want communications in a separate conduit above the electrical in the same trench.
Go big on the conduit...as you learned with the old conduit...If you want to run communications or 50amp line later, it's much easier if you have a 2" or even larger conduit to work with and the cost difference is negligible.
Aug-14-2018 02:47 PM
Macrosill wrote:
I just did this last week. I trenched and laid 1" pvc. I had lots of 10 awg thhn on hand so I ran 2 parallel sets of it to minimize the voltage drop. Paralleled 10s came in with less voltage drop then 8 awg did and the copper was free.
Now before anyone gets their pants in a twist I know I am using smaller than 1/0 conductors but there is an exception in the NEC provided all the conductors are in the same conduit and the condcutors are sized than any one of them can carry the full load should you lose one. They are all in the same conduit and they are all 10 awg.
Aug-14-2018 09:04 AM
valhalla360 wrote:You’ll want communications in a separate conduit above the electrical in the same trench.
Go big on the conduit...as you learned with the old conduit...If you want to run communications or 50amp line later, it's much easier if you have a 2" or even larger conduit to work with and the cost difference is negligible.