Looking into installing 30 TT outlet on my detached garage

Problem is that it is about 90-100 feet from the home circuit breaker box. Voltage drop calculator has about a 5% voltage drop for that distance using 10awg and about 3.5% using 8awg (not allowing for the TT shore power cord).
I'm thinking I'll need to use 8awg.
Copper gets expensive, plus added components, outside jack, ditchwitch rental, etc.
Any thoughts?
I'm looking at Direct Burial wire or interior grade that would be routed through sealed plastic pipe. I've only checked Home Depot pricing so far and not the local electrical supply house.
Garage has 12awg run to it and is a good 110-120 feet run through the house and ground from the CB box.