Chum lee wrote:Nope. When combined in series, the voltage increases, but the capacity does not.
The standard book answer is: the amp-hr rating divided by 10. I know many people will argue with this.
So, if you have a pair of 232 Ah 6 volt deep cycle GC batteries in series that would be:
232 + 232 = 464 / 10 = 46 amps initial charge rate @ +- 14.8 volts or higher.
โAug-16-2017 11:20 AM
mike-s wrote:
Note that manufacturers recommend limiting the charge current. Trojan says 3-5% of C20 (so about 11A for a 12V pair of GC2). US Battery says 10% of C20, Rolls and Crown say 10-20%.
โAug-16-2017 10:53 AM
โAug-16-2017 10:48 AM
โAug-16-2017 10:32 AM
โAug-16-2017 10:11 AM
โAug-16-2017 09:31 AM
โAug-16-2017 08:51 AM
brulaz wrote:that also depends on the battery bank. Is this a pair of GC2's, or 4?
Say the GC2 battery bank has been drawn down to 25-50%, what will be the max current they will initially accept?
For sure it's greater than the ~24A max my solar charger has reported as that was limited by the solar panel outputs.
โAug-16-2017 06:28 AM
red31 wrote:
If ya extrapolate both sides of BFL's ugly graph, I suggest 90-100A would get the battery to 14.4v in short order and then taper from there.
...