Norcold 1200 refrigerator fan wiring question

I have a pre 2006 Norcold 1200 refrigerator that the two cooling fans on the condenser ceased operating after the refrigerator was worked on for a heating element problem.

Research has led me to believe the tech installed the black and white wires that supply 12 volts to the fans incorrectly.

If someone who has a 2005 or older RV with the Norcold 1200 refrigerator could look at their control board tell me how their board is wired I'd sure appreciate it. There are two wires that go to the fans....a black and a white.

As you look at the control board is the black wire on the right or left connector?

You can see the wires without removing the cover on the control board.
  • Ivylog wrote:
    I doubt it makes any difference...try reversing the two wires. Too bad a pair of wires were not run from the temp switch so you could manually turn on the fans to test.


    That's what we have always done; run the fan wires directly to a simple on/off switch mounted inside the rv on the wall close to where the fan(s) are.
  • ArchHoagland wrote:
    dougrainer wrote:
    Yes, IF the 2 wires are reversed the Cooling fans will not operate. VERY common mistake novices make. If all the tech did was r&r the Heating element, just reverse those 2 wires. I cannot remember which is which. I have that info at work. Doug


    The Norcold manual has a picture of my control board showing the white lead on the left.

    Mine has the black wire going to the left connection.

    There is 5 volts DC on that connection.

    Could you please check at work and determine if, indeed, the white wire should be on the left terminal.

    Thanks.


    Just swap them. NOTHING bad will happen. The ONLY thing that happens when they are reversed is the fans do not operate. Since yours do not, the logical thing to do is swap them. Doug
  • dougrainer wrote:
    Yes, IF the 2 wires are reversed the Cooling fans will not operate. VERY common mistake novices make. If all the tech did was r&r the Heating element, just reverse those 2 wires. I cannot remember which is which. I have that info at work. Doug


    The Norcold manual has a picture of my control board showing the white lead on the left.

    Mine has the black wire going to the left connection.

    There is 5 volts DC on that connection.

    Could you please check at work and determine if, indeed, the white wire should be on the left terminal.

    Thanks.
  • dougrainer wrote:
    Yes, IF the 2 wires are reversed the Cooling fans will not operate. VERY common mistake novices make. If all the tech did was r&r the Heating element, just reverse those 2 wires. I cannot remember which is which. I have that info at work. Doug


    Bingo
  • Yes, IF the 2 wires are reversed the Cooling fans will not operate. VERY common mistake novices make. If all the tech did was r&r the Heating element, just reverse those 2 wires. I cannot remember which is which. I have that info at work. Doug
  • Ivylog's avatar
    Ivylog
    Explorer III
    I doubt it makes any difference...try reversing the two wires. Too bad a pair of wires were not run from the temp switch so you could manually turn on the fans to test.
  • Fans wires??

    Fans are supplied via circuit board
    12V DC POS goes to thermostat on condenser fin and then to fan
    12V DC Grd comes from fan back to board

    12V DC POS (should be black) would be LEFT
    12V DC Grd would be RIGHT

    Thermostat....Closes when condenser fin temp reaches 130*F and Opens when condenser fin temp drops to 115*F