Fans are thermostatic controlled. Thermostat is on condenser --turns on fans when fin temp is 135*F and turns them back off when fin temp is 115*F fin.
NO fans should not be running in low ambient air temps (usually not needed below 85*F air temps)
The 2 heaters are 225W/EA (450W) so a bit low at 415W
Air flow is needed (Draft) to remove heat from cooling unit.
Blocking off a couple of vents and using a 60W bulb helps when temps are below freezing....but not completely blocked off.
A quick visual for gas pressure......turn on all stove top burners on high. Watch each as you turn on another one. Flames steady/remain at same height or do the diminish height?
Now with them all running turn on furnace or water heater.
Do they recover? If not........LP pressure needs adjusted.