Normal to have to 'bleed' propane system after non-usage
BUT you are NOT bleeding AIR out of the system.
When all propane appliances are tuned off the LP Reg goes into 'lock-up' mode to prevent HIGH System pressure (static)
Then when placing system back in service the REG needs to come out of 'lock-up' status and establish flow----need a demand to do so.
At 11"WC (0.4psi) establishing that FLOW thru out the system can take several minutes and lines to each appliance will need to have flow fully established by those individual appliance gas valves opening.
Some will require several attempts due to appliance gas control/flame sensing.
Stove top is easy due to NO flame sensing ----turn knob, spark/match and light the flame.
That first demand palces REG in service and starts establishing flow
Propane has a narrow ignition window and until proper flow is established the air/fuel mixture will be unbalanced so it may seem like 'air' is coming out but it really is propane at low pressure which needs to come to full sstem pressure so that the correct air can be pulled in thru appliance burner 'air' inlets to mix with the propane at full pressure for correct combustion ratio
NO AIR.....just low propane flow/pressure
Absolutley NORMAL
Is it time for your medication or mine?