Rogue 20A MPPT Controller Question

mena661
Explorer
Explorer
Maybe Marc will chime in but maybe this question is generic enough that others might answer. I was perusing the Rogue 20A manual and saw the 320W limit for 12V systems. I'm wanting to put two 150W panels in series to up the volts and reduce current in an attempt to be able to use more panels on the controller at a later date. If my total amps is well under 20, can I go beyond the 320W max for the controller?
18 REPLIES 18

mena661
Explorer
Explorer
Thanks Almot. I'm just going to use one of the built-in presets for the time being. No need for the data converter just yet.

Almot
Explorer III
Explorer III
mena661 wrote:
I was perusing the Rogue 20A manual and saw the 320W limit for 12V systems. I'm wanting to put two 150W panels in series to up the volts and reduce current in an attempt to be able to use more panels on the controller at a later date. If my total amps is well under 20, can I go beyond the 320W max for the controller?

You can, and you should. What you should also do, is get Rogue 30 instead of 20, especially if you go beyond 320W :)...

Rogue 20 will clip the output amps at 20, maybe 21A.

300W array under ideal conditions will output about 10A @30V. After the conversion to 13.5V, 10A becomes 22A. Ideal conditions don't happen at sea level, so you are OK with Rogue 20, but pretty close to losing some power. If you increase the wattage beyond 300 or 320, you will likely lose some power at peak sun (compared to if it were Rogue 30), but you will still get more power than with 320W, because most of the day there will be no clipping as your amps will be below 20.

Rogue 20 requires data converter or remote display to change any settings because it has no interface display like Rogue 30. So the difference in price is not that big.

BFL13
Explorer II
Explorer II
mena661 wrote:
BillyW wrote:
Does anybody know how (well) the Tracer temp compensation feature works?
Not sure, I was that mysterious someone that BFL was talking about would post his findings on the Tracer.


Mena the guy said he went ahead and bought a Tracer and would test it for us sometime early this year. From back east somewhere ISTR. I will do a search.

It was hmknightnc

http://www.rv.net/forum/index.cfm/fuseaction/thread/tid/27359688/srt/pa/pging/1/page/2.cfm
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

mena661
Explorer
Explorer
BillyW wrote:
Does anybody know how (well) the Tracer temp compensation feature works?
Not sure, I was that mysterious someone that BFL was talking about would post his findings on the Tracer.

TurnThePage
Explorer
Explorer
Does anybody know how (well) the Tracer temp compensation feature works?
2015 Ram 1500
2022 Grand Design Imagine XLS 22RBE

mena661
Explorer
Explorer
If the Tracer works well then it's a good deal IMO.

BFL13
Explorer II
Explorer II
Yes, quality assurance is worth a lot and the price difference is little more than a tank of gas for the truck which nobody blinks at. Also it's only a one time thing soon forgotten, while the truck keeps wanting more ๐Ÿ˜ž

One of the members ISTR on the East Coast said he would report on the Tracer. That 100Voc gives it a big advantage over the 20a EcoW at 42Voc if you wanted to use two 12s in series which you can't with the EcoW.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

mena661
Explorer
Explorer
smkettner wrote:
300w and 20a controller will serve you well.

If you expand in the future... cross that bridge when you get to it. It might be a second 20a controller or a replacement 60a controller. Might be higher open circuit voltage MPPT needed or high amp PWM depending. Expansion system may not series or parallel well with existing panels. Too many future what ifs. Load that 20a with 300w and enjoy.
Good points smk! I just might need more than 10A for expansion next go round and a second controller may just make more sense. And it will save me $100 towards panels.

BFL13 wrote:
I was thinking cheaper MPPT too like the Tracer if you don't want all the fancy data stuff and laptop connections etc which have nothing to do with feeding the batteries but do provide geek entertainment ๐Ÿ™‚

A 20a, 100Voc Tracer is about $140
You know I didn't think I wanted all the fanciness but at $275 for the Rogue 20A, it's not too much considering what you get plus Marc is really helpful here. I'd like to support his company. Plus I worry about the cheaper units shutting off in the summer like the Iota converters do.

time2roll
Nomad
Nomad
300w and 20a controller will serve you well.

If you expand in the future... cross that bridge when you get to it. It might be a second 20a controller or a replacement 60a controller. Might be higher open circuit voltage MPPT needed or high amp PWM depending. Expansion system may not series or parallel well with existing panels. Too many future what ifs. Load that 20a with 300w and enjoy.

BFL13
Explorer II
Explorer II
I was thinking cheaper MPPT too like the Tracer if you don't want all the fancy data stuff and laptop connections etc which have nothing to do with feeding the batteries but do provide geek entertainment ๐Ÿ™‚

A 20a, 100Voc Tracer is about $140
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

mena661
Explorer
Explorer
BFL13 wrote:
In the manual above the 320w recommended limit guide it says:

"....... Conversely, an array that is oversized will constantly push the MPT-2024 to its maximum limit of 20A. At and beyond this limit the power from the array is constrained and the MPPT algorithm is overridden so that the controller does not exceed its maximum current output. To avoid wasting available power, follow the guidelines given in Table 4.4.1 when sizing your array."
Maybe I should read the whole manual next time. ๐Ÿ™‚ Thanks all, I'll get the bigger controller. And, yes, BFL I could get a cheaper (with higher amps) PWM Morningstar but I'm not sure if I'll be adding anymore panels. I'd have to do some more measuring on the roof to see if I could get more up there.

CJW8
Explorer
Explorer
Mena,
I live in AZ. I have checked my controller when it was 100+ out and the sun directly overhead many times with no excess heating observed. My son is a solar installer and I have watched him size many systems including two of my home systems. It is very common to size the PV array larger than the inverter.
2003 Forest River Sierra M-37SP Toy Hauler- Traded in
2015 Keystone Raptor 332TS 5th wheel toy Hauler (sold)
2004 Winnebago Vectra. 2011 Jeep Grand Cherokee toad

KJINTF
Explorer
Explorer
Hi mena

MPPT controller rating = Input Power (w/ a max voltage limit) & Output Current

When the input power rating is exceeded (on quality controllers) typically the integrated "Processor controlled TRACKING function" is used to reduce the input power level, which then limits the output current to within the system specifications.

Many folks run a higher power array than the controller is rated for with out issues.

I suggest you do NOT
Instead oversize the controller
This oversize allows for -
Future array expansion
No wasted energy when the "clipping" occurs, wasted $ on power that is not used
Reduced heat - higher the current higher the internal heat generated
Longer life from running cooler
Generally just a better system design

westend
Explorer
Explorer