Old-Biscuit wrote:
Only way to have 13"WC AFTER the stove reg is for the UPSTREAM pressure to be high .....main lp reg has failed or set at 14"WC +
Stove reg should be set for 10"WC with upstream pressure set for 11"WC
Should be test port on Fridge shutoff valve that would show LP System pressure
Main System pressure must be tested/adjusted PRIOR to checking stove reg pressure
Stove reg can be adjusted//just have to remove plug in center stub
The main regulator is brand new. Maybe I need to turn down the pressure from it. I will check my fridge for the test port. Can I adjust the main regulator from the readings I get before the stove regulator?