Forum Discussion
ps2000
May 06, 2019Explorer
Old-Biscuit wrote:ps2000 wrote:Old-Biscuit wrote:
Only way to have 13"WC AFTER the stove reg is for the UPSTREAM pressure to be high .....main lp reg has failed or set at 14"WC +
Stove reg should be set for 10"WC with upstream pressure set for 11"WC
Should be test port on Fridge shutoff valve that would show LP System pressure
Main System pressure must be tested/adjusted PRIOR to checking stove reg pressure
Stove reg can be adjusted//just have to remove plug in center stub
The main regulator is brand new. Maybe I need to turn down the pressure from it. I will check my fridge for the test port. Can I adjust the main regulator from the readings I get before the stove regulator?
NO.......
Main reg has to be adjusted BEFORE checking/messing with stove reg
Using pressure reading after stove reg gives you no true reading of upstream pressure
Adjust it down so stove pressure is 10"WC and you could only have 10"WC Upstream
Adjust Main reg measuring main system pressure
Then check stove reg pressure and adjust IF needed
Ok. I will try adjusting the main regulator pressure. I will set it to 11"wc and see what the stove regulator does.
About Technical Issues
Having RV issues? Connect with others who have been in your shoes.24,192 PostsLatest Activity: Jan 26, 2025