myredracer wrote:
Besides what's already mentioned, voltage can be part of the issue if you're are running an AC unit. Low volt causes an AC unit to draw more current and then cause more heating at the plug/receptacle connection.
Not in this case.
While low voltage can sometimes cause an AC to draw a little more current, it's only in the neighborhood of a couple of amps. That would make a total that is far under the 30A circuits capacity and well within the capacity of the plug. Even if the OP were dwawing way too much power, the fact that the plug is hot tells us it's the problem. It should pass current fine and without excess heat right up until the breaker trips.
Excess heat at a plug is caused by a poor connection
at the plug and not by a couple of extra amps pulled by the AC.
OP, you should certainly monitor the voltage level but your issue is with the receptacle.
The heat always comes from the weakest part of the circuit and those 30A receptacles are notorius for being worn.
Best advice here is the 50 to 30 dog bone.