Furnace problem

My furnace worked fine last Thanksgiving. Made a little trip this week and it got down into the 30's. Turned on the furnace and here is what happened:

Blower turned on,
I heard the burner ignite,
ran for a little while,
burner and blower stopped at the same time,
few seconds later the blower came on,
burner restarted,
ran a little while and the cycle repeated,

the amount of run time was not the same it varied from a few minutes to a few seconds,

After a several cycles I waited for the burner and blower to stop and then switched the unit off at the thermostat. The blower then came on to cool the heat exchanger and then turned off.

Any ideas?
  • If the burner and the blower motor are stopping at the same time, it appears you are loosing the 12 volts to the furnace. The blower motor should never stop during the burn cycle. Please post the model of your furnace so we can look at your specific wiring diagram and give you some more advice. Wiggle the wire connections at the furnace and see if you can duplicate this motor stopping problem during the initial start cycle.
  • use a wire brush and gently clean the area by the igniter and also any flakes of corrosion and then try to light it.
  • One of the common things that I have found is the connection to the ignitor is corroded. It is good enough for it to ignite the gas but, not good enough to get the burn signal to the board. Try removing the connector from the ignitor and then reinstall it and wiggle it around a bit. If that doesn't fix it, pull the board and have it checked at an RV repair facility.
    Good Luck