bcbob wrote:
Thanks to all that have responded. I’m going to start with what works. I have two GFCIs in the coach. One on the bathroom vanity and the other one under the dining table. When I start the generator all outlets on the dining room GFCI work. The vanity GFCI ( new ) will not reset so there is no power to the outlets on that GFCI.
To deandec… yes to everything.
To enblethen ……244 and 122 at the breakers. All 50 - 30 - and 20 AMP breakers are on with 244 and 122 volts flowing thru.
I took the cover off the transfer switch. I had my wife start the generator while I am at the TS. I heard it “switch” and the green light came on. I shut the generator off ( already unplugged from shore power ). I turned the inverter on and I get no volts at the TS or CBs. I think we are getting zeroed in but the mystery to me remains why current flows thru the dining GFCI when the generator is on but not to the vanity GFCI ? Why no current to any outlets when plugged into shore power when all breakers read 244 and 122 ? TS is sending current to CB panel. Could the TS not switching to invert be the cause of all this?
your breaker is tripped on your inverter or your inverter is bad
I had to bypass my neigbours inverter because there was no flow through power when on shore power but I never tried it on gen power.As it turns out the 120V sensor was bad in the inverter
Do you have two 120V circuts flowing through your inverter or one?