No coach 110v power when connected to shore line

New problem today (gotta love 25 year old appliances)

Connecting the shoreline to a 110v source (eg. home extension cord), I've got no power to the coach. Was working 2 days ago and I have not done any electrical work.

Symptoms:

- connecting shoreline provides NO power to the AC circuit / main breaker of the power distribution panel; I also don't hear the transfer switch relay tripping either anymore

- starting the generator does trip the transfer switch and the AC circuit energizes as normal

- when connected to shore, I've tested 110v energized all the way up to the automatic transfer switch box connection, right on top/back of the distribution panel, but no power at the breakers hot bus, so I am suspecting the relay inside the transfer switch

the ATS/Power Distribution Panel is one of these:


Can these things be repaired? or am I looking at needing a new ATS/panel?