Remove 50amp genset and replace with 50 shore power

Since I have a 96 class A with a 30 amp service but a 50 amp genset that would run both AC units. I would like to remove the generator and wire in a 50 amp shoreline so I can run everything. Does anyone see a problem doing this as long as the proper materials are used?

23 Replies

  • 30 amp shore cord and breaker panel
    One each hot, neutral, ground 10 gauge wire

    Generator possible wiring, very common
    One neutral, one ground , two hots
    One hot goes to ts stitch and breaker panel for 30 amps
    Second hot goes only goes only too the second a/c

    50 amp shore power
    One neutral, one ground, two hots, all wires are 6 gauge
    It is 50 amps on each hot, 100 amps total

    This has nothing to do with removing the generator
    You can Not just remove generator and splice wires to new shore cord
    You need new breaker panel, new wire from panel to the New TS, all the way to the New shore connection
  • Sorry, makes no sense. If 50 amp generator (never heard of them being rated in amps) why not just leave the generator in place and replace:

    Shore power cord

    Wiring from shore power cord to ATS (assume you have an ATS-- if not to a new outlet that generator can be plugged into)

    New wiring from ATS to main 120 VAC breaker box

    New breaker box with 240 VAC/two HOTS inputs.

    This AIN'T for the faint of heart or on a small budget. There are other options, but this would be the "automatic way"-- the way a 50 amp coach would have been wired from the factory.