- MrWizardModerator30 amp shore cord and breaker panel
One each hot, neutral, ground 10 gauge wire
Generator possible wiring, very common
One neutral, one ground , two hots
One hot goes to ts stitch and breaker panel for 30 amps
Second hot goes only goes only too the second a/c
50 amp shore power
One neutral, one ground, two hots, all wires are 6 gauge
It is 50 amps on each hot, 100 amps total
This has nothing to do with removing the generator
You can Not just remove generator and splice wires to new shore cord
You need new breaker panel, new wire from panel to the New TS, all the way to the New shore connection - wolfe10ExplorerSorry, makes no sense. If 50 amp generator (never heard of them being rated in amps) why not just leave the generator in place and replace:
Shore power cord
Wiring from shore power cord to ATS (assume you have an ATS-- if not to a new outlet that generator can be plugged into)
New wiring from ATS to main 120 VAC breaker box
New breaker box with 240 VAC/two HOTS inputs.
This AIN'T for the faint of heart or on a small budget. There are other options, but this would be the "automatic way"-- the way a 50 amp coach would have been wired from the factory. - 2oldmanExplorer IIjust to verify, what is the make and model of the gen?