Rooftop ac repair

Ok both my rooftops are not working. Dometic Duro Therms.
Took covers off and installed peircing service valves. Both had no freon. Both had pin holes in capillary tube in same place apparently rubbing issue. Cut sheet metal to access. Put a drop of braze on one and cut one out and sleeved with a peice of 1/4 inch tube and brazed. Pulled a vacuum on both and filled both with 24.5 oz of r22.
Wasn't very warm but shot the rear plastic ac grate with ir gun 67* fired up generator turned rest ac an feels cool 15 min shot plastic ac grate again in same spot 48*
Shut down rear and started front. Fan comes on but compressor keeps on trying to start every minute or so and cuts out. Removed wires from compressor and all have continuity. Switched all capacitors and compressor over load switch from working rear to front and no change. I guess compressor is locked up. Was thinking of trying a hard start kit but not sure it would work. Was thinking about trying to find a compressor but a quick search showed nothing. Gotta hop back on roof and get numbers off it. Here's a few pics.







  • newman fulltimer wrote:
    Those av units don't run on r22 is the first problem



    Hmmm pic of compressor and my owners manual were I found how much freon it takes



  • If you are talking 1998, then Freon 22 is the Freon to use. BUT, most units use only 16 to 20 ozs of Freon. HOW did you determine the correct Freon fill capacity? There are only 2 ways to fill a Roof RV AC
    1. Dial a Charge
    2. Temp corrected amp draw AT the compressor
    Regardless, your Compressor is not caused by your fill. You have a bad compressor. YES(or NO) you will not find a replacement Compressor for a RV Roof AC unit. They have not made replacement compressors for more than 30 years as it was cheaper to replace the upper unit complete than pay to replace the compressor. Doug

    PS, since you are handy brazing the lines, LEAVING the Line taps on is foolish. You only install Line Taps to safely(EPA) drain any possible Freon still in the system and then braze the Line Tap pin holes and braze in standard copper Schrader valves. Line Taps WILL LEAK. Eventually.