Bikeboy57 wrote:
I tend to agree that you have a generator issue. Especially since the ATS was replaced and the behavior did not change. I would disconnect the gen leads at the ATS and measure the voltage behavior on the disconnected leads. That will take
The ATS out of the equation. If the voltage is varying at the disconnect leads, then measure at the junction box located at the gennie
Tested at junction box- 120.3,120.5
Made connections moved to ATS
Tested at ATS Genny wires only 120.4,120.3
Hooked wires back into ATS fired genny measured at lugs
120, 119.3
Clunk volts keep dropping until 65,- 70 then clunk and they build again, until ATS is satisfied and it opens again...repeats....