Forum Discussion

Meffrig's avatar
Meffrig
Explorer
Apr 02, 2017

Surge protector question

I went to my favorite park and plugged in as always to the 50 amp pedestal and my built in surge protector would not allow the coach to have power. The nice folks at the park came out to help and checked the power which showed fine.. They had changed out the breaker to 60 amp. I even tried reducing the power down to 30"amp with no luck. I moved to a different site with a 50 amp breaker and my power came thru. By changing the breaker in the pedestal, did this keep me from getting power on my original site? Also, my surge protector makes a popping noise when the power in the coach kicks on. Is this normal? Any advice is much appreciated.
  • Meffrig wrote:

    I went back to the campground today. They are replacing some of the 50 amp breakers with 60 amps as needed.The campground handy man told me some of the new larger Class A busses are now all electric. He assures me that the pedestal is hooked up properly because all he did was change the 50 amp to a 60.


    So they're using 60A breakers with 50A receptacles? That in and of itself is not hooked up properly and is a violation of the NEC which, I assume, is the locally used electric code.

    If all that was done was replacing the breaker, it would stand to reason that a problem in the neutral or ground wiring of the socket would still remain. Changing the breaker hardly seems to me to prove that the pedestal is or was wired properly.

    At any rate, I wouldn't put much faith in the opinion of the handy man in this case. He's showing that he has at best a limited understanding of electrical work, and possibly knows only enough to be dangerous. (I certainly don't mean to suggest that he's attempting to mislead you, or that he doesn't mean well, or that he's doing anything other than the best he can. It only appears that he's none too well qualified on electrical matters.)
  • My surge protector is Surge Guard, model 34560. Line 1 and Line 2 light up in green and the Caution When Flashing Light blinks in red while checking the power from the pedestal. I should have 3 green lights,( no red) when all is OK. I have my unit hooked up to a 15 amp outlet at home just to keep my batteries charged with no problem .

    I went back to the campground today. They are replacing some of the 50 amp breakers with 60 amps as needed.The campground handy man told me some of the new larger Class A busses are now all electric. He assures me that the pedestal is hooked up properly because all he did was change the 50 amp to a 60.

    This has really got me puzzled. I will continue to try to find the solution because I really like the campground and the people there.
  • The surge protector will not pass power for multiple problem. Low or high volts, open neutral, open ground or a swap of one of the hot lines with either the neutral/ground are the bigs. As mentioned the protector just paid for itself and the CG needs to find a better electrician.
  • Plug int a power pedestal that has been worked on by cg 'electrician; and surge protector does NOT allow power to your RV

    Then you plug into another power pedestal and your surge protector allows power to your RV

    Answer is obvious .....1st pedestal is not wired correctly


    Popping noise when SP allows power thru???
    A 'click' noise is common/normal...but a popping noise. That doesn't sound right

    Which Brand...TLC Surge Guard (1 yr limited warranty) OR Progressive Industries (Life Time Warranty)
  • No error message on my surge guard. I just got the flashing red light-- and no power. I even tried reducing down to 30 amps with no luck.
  • The first site probably had a problem with the wiring of that new 60A breaker. They probably got something swapped at the plug or had a missing neutral.
    What ever the case, your SP probably saved you from some damage.