dcs1968 wrote:
Well I just got off the phone with tech support at Harbor Freight and for $22.43 I ordered an AVR and $2.92 a set of carbon brushes. Crossing my fingers that this will fix it. Thanks for the help.
Two types of voltage regulation are common on the 3,000 watt Chinese Gensets. Those that use a capacitor as a regulator do not have a brush set. Those that use a AVR or automatic voltage regulator will have a brush set. It is doubtful that your brushes have worn out. A more common problem is AVR failure due to too much heat. Since you were in the desert this seems likely. To cool the AVR air must be pulled over the module at the end of the generator shell (painted end cap). Air is pulled into the generator (actually an alternator) by a fan at the front of the generator shell next to the engine that has its outlet pointing down. When an AVR fails it is more common to have an extreme voltage rise - sometimes as high as 170 VAC. The loss of any voltage output can happen with AVR failure but is much less common.
Please post the results after you replace your AVR. If regulated output returns you might want to consider some of the modifications forum members have implemented to increase AVR cooling.