All 3 of my batteries were bought in the same month....just adding them to the trailer permanently with some 1/0 cable.
not going to make much difference, 2-3 years max and you will be replacing them anyway..
Oldsmokey, still waiting to hear your reason why my brand new AGM batteries will only last 2-3 years?????
sorry for the delayed reply, I have been overseas finishing up a contract.
now back to your issue, i'll try to keep it in laymans terms.
your Duracell agm is a budget agm made by interstate, it's a 'b' grade and not
made to the best standard. battery to battery variance in internal resistance and
capacity is the issue here, when you connect them in parallel the set will behave
( performance wise ) as the worst battery. so in effect you had 2 good batteries
and one not so good and made them into three not so good batteries.
now the situation becomes worse when you actually use them and start to charge and discharge
over time.
for this example your batteries numbered 1,2 and 3 are connected in parallel string
with the take off on battery 1 to your equipment.
you now discharge at 90 Amps. you would think that each battery will supply
30 amps right ?.. well your wrong,
in practise, more current will be drawn from batt 1 than batt2 and batt 3
this is due to cable and internal resistance.
i won't bore you with complex network analysys, but the current distribution
from a 3p string is approx like:
batt 1, 41 A
batt 2, 28 A
batt 3, 21 A
so you have batt 1 doing much more work than batt 2 and batt 3
this also happens when charging, batt 1 will charge first with the others lagging
behind. now, after many cycles of this abuse, batt 1 will age much more rapidly than
batt 3. as batt 1 ages, it has the effect of dragging the others with it as they
attempt to equalize each others voltages. batt 1 drags batt 2 and 3 and batt 2 drags 3
now for fun, just imagine what happens if one battery cell develops a short ??
you guessed it.. the others dump their charge into it at a very high rate
and you get your very own firework show..
now there is a 'trick' that will mitgate some of this and it's simple..
you connect all 3 in parallel and draw positive from one end of the string
and neg from the other.. now you only have one batt underworked..
it's still not good but will give the string a better chance..
you stated you have 360 W of panels..
I can tell you right now that's not enough.. 300Ah of agm will need
at least c/10 to charge. a good mppt cc will be 90% so 360 * 0.9 = 324 W
and 324 W at 12V = 27 Amps.. so you are short even at max insolation.
you need a minimum of c/10 or better still, for agm c/6 = 50 Amps
so you need more like 720 W or so.. and that's probably wrong because we don't know
your actual usage.
and fwiw, that WFCO convertor is not woth the space it occupies and will not
charge your agm's correctly either.