advice to install 30A RV Receptacle in garage to power RV

I would like to make my 34 footer RV into a man cave when I'm not using it. :) I need to put in a 30A 125V RV receptacle so I can connect the RV to the house power.

As far as I know, this is what I need:

1. Junction box/cover plate and the 30A rv receptacle (TT-30R?)
2. 10 gauge electric wire
3. 30A breaker? What kind/type?
4. and a 100ft 30A rv extension cable?
Can I use the cheaper house electric cable rated for 30A and just the adpater?

Any help is much appreciated.

I don't want to pay $400 to the electrician.
  • uclabruins wrote:
    There is a 220V line located outside the house that is powering the well. I think I can split it to get 110V 30A. Is this safe?
    Probably not. Probably no neutral to get 120v. Even then the circuit was installed to power just the pump. Adding a 20 to 30 amp load on one side may trip the breaker too easily.

    http://www.myrv.us/electric/ Click the 30 amp link on top left.
  • There is a 220V line located outside the house that is powering the well. I think I can split it to get 110V 30A. Is this safe?
  • In reply to question #1 & 4: Junction box will need to be weather proof if it is exposed to elements. Where will the cable be located? Inside a building, overhead on poles, or under ground? An inside cable can not be used underground, or overhead.
  • Make VERY sure that person who wires the box and outlet KNOWS that it MUST be 110 Volts. Even "skill" electricians have wire as 220 Volt. Don't ask how I know.. . . . . :M . . . . :M
  • Use Romex for unenclosed circuits, individual wires when doing it within EMT conduit.

    The OP asked about 120vac receptacle installation so I'll stick with it.

    If the receptacle is going to be located within 30 twisty-windey feet of the main breaker box 10 gauge is a minimum. I like 8-gauge better. I have with me own eyeballs checked the voltage difference between the two wire sizes and for A/C hot restart with a good converter load, the voltage remains notably higher using #8.

    After installation recheck ALL wire connections and re-tighten after 6-months. Let me know if you find any connections that could not use a re-tightening.
  • Call an electrician. They will do the work, and it will be done right.
  • Not sure about the parts but I would put in 50 amp who knows when you might trade in your current rig

    I had my 50 amp put in professionally