A bit more follow on info. But first, at 3:00PM today, again after the ongoing repeating of the Equalize/Condition four cycle at 14.4V, the Amp reading went up from 15 to 17 Amp. I thought yesterday just before noon, I saw the Amp number jumping/fluctuating quickly between 14.5 to 15 Amp - but perhaps it was wishful thinking:)! It never 'settled' below 15A at anytime that I saw.
On battery temps. The four batteries are locked down tight into a rectangle configuration, actually if you look at the smaller rectangles of each battery, their four rectangles, making one larger rectangle. The longer side of the rectangle is facing the battery compartment opening. So I have long side of two batteries facing me, and was shutting the infrared at the top in the middle cap like item on each cell, and then I also went down the front side of the battery on each cell of these two batteries. With todays low to mid 80's outside, the temperatures read 86.0F + or - .4F degrees between cells. The middle cell, as well as the two end cells that were next to the each other between the two batteries, were usually the .4F degree higher then the outside end cells. I do want to clarify the four batteries are not in direct contact with each other, a little under half inch spacing between each battery.
I could read the top of the back two batteries, and the same variation, but the + or - varied by .6F, I could also shoot the end of one of the back two batteries (The other is too close to the side of the compartment to get a shot.) and all up and down the end cell. it was within .1F of the reading I got on the top of that cell.
Ok, so now a wonder I have, and could not find in the Magnum manual. Is it possible the Equalize phase is set to never drop below 15A?
And right or wrong, I've stopped the feed of 14.4V when I saw for the second time, the Amps going up a bit, and never seeming to drop below 15A. I'm a layman for sure compared to many of you on this forum, but my thinking was I'm probably doing the batteries no good by doing all of this... If they've had the bulk of their magic juices consumed - concerned I've just been consuming more of the little that maybe left.
For grins, I turned on both the MidNite Classic 150 controller, and set the Magnum back to normal Charge mode. Within 15 mins, both were showing Full (Magnum) or Resting (Classic) And both indicate 100% SOC.
I did reset my Magnum recorded life of battery (Well, last 4 1/2 years with the Magnum in.) Max AH Out to zero. It was 4259.2, which is easier just rounded up to 4800 to some what account for the first 6 months. (Very little usage during that six months, as we were not retired then. The coach was plugged in and maintained by the previous 3 stage charger, set as close to the Lifeline parameters as possible. So that is probably more AH Out then actually occurred during that 6 months.
Help me with the math on this gang.
Lifeline says rated at 1000 DOD Life Cycles at 50% utilization.
50% of 800AH bank is 400AH per cycle
400 x 1000 - 400,000 AH's over the life expectancy of the battery in ideal circumstances
Since ideal circumstances are not a reality. Being conservative I'll use 300,000 AH's available
Rounding up as I did to 4800 AH Out, heck add another 1200 for extra cushion and say 6000 Max AH Out
6000 used is no where near 300,000. Using the Lifeline Tech call reviewed and supported OK of the Magnum Lifeline AGM1 setting - I remain convinced the battery bank had an easy life. (Or, like to think so.)
Is my thought process correct on the above?
I do have an email into Lifeline, and have not heard back from them yet.
Oh well, real test will be tomorrow night when the sun goes down, and generator hours are over here in the park. We'll see if the last few days of Multiple Conditioning and the last mostly steady 14.4V feeding.
It will be, what it will be:)!
Best to all,
Smitty