I've completed the build of my converter upgrade using RoyB's schmeatic (below) and I have an issue that I think I have the answer to but want to run it by the forum.
I've blown the 125amp ANL fuse twice now, both times on battery power while raising the auto-levelers which I assume must use a lot of juice. The fuse protects the wire between the converter and the 12 volt distribution center.
I believe the 20' run from the batteries to the 12 volt distribution panel using the stock 6ga wire is too long for the wire size. The converter can accept up to 2ga.
Just want to see if replacing the run with 2ga or even 4 ga will fix my problem before I drop the coin.
I've blown the 125amp ANL fuse twice now, both times on battery power while raising the auto-levelers which I assume must use a lot of juice. The fuse protects the wire between the converter and the 12 volt distribution center.
I believe the 20' run from the batteries to the 12 volt distribution panel using the stock 6ga wire is too long for the wire size. The converter can accept up to 2ga.
Just want to see if replacing the run with 2ga or even 4 ga will fix my problem before I drop the coin.
RoyB wrote:
I upgraded my real old single mode converter/charger to a WFCO 45AMP smart mode converter/charger only to find out I could never get my WFCO unit to go into smart mode charging.
Then I purchased a PD9260C 60AMP smart mode converter/charger but I mounted it stand alone closer to the battery bank. I decided to leave the WF8945 unit in its location in the bottom compartment of the WF series Power Distribution Panel.
I ran a 120VAC connection to the PD9260C from another circuit breaker in my panel.
I most of the time use the PD9260C by just flipping the circuit breaker for this unit and have the WF8945 converter turned off by flipping its circuit breaker.
I only have the brand new WF8945 converter around for back-up purpose. I only have one converter turned ON at a time however I don't think it would harm anything having both of them on. It just didn't seem like having two converter units ON at the same would be a good idea.
You can see where my two converters are installed in this floor plan drawing of my trailer...
This is a schematic diagram of my how my two converters are wired in my setup...
There is some posts on here where a B&D VEC1093DBD smart mode portable battery charger was being used along with the on-board trailer converter/charger to get to full 100% charge state on the batteries quicker.