Common trip breakers have always been required on 220v circuits like the 50A here, but only recently (last couple years) required on split 110v circuits that share a common neutral. see diagram here, a different animal than a 50A circuit.
Somewhat recently, probably depending upon where you live. When I sold my 1978 house in 2003 the buyer's inspector marked down shared neutral (15A) circuits that were on seperate breakers. I replaced them with common trip ones.