mperkins52 wrote:
Hi Doug ..... if I understood you correctly, the white wires should be on the left (FLPR_HEAT) and the black wires on the right (FLPR_GND) ... if that is the case then mine is wired correctly .... there must be a problem with the thermostat ..... replacing that may be the next step .... I removed the top today and access to the thermostat appears to be pretty easy. If I do that I may as well add so extra fans to help cool the condenser fins .... any other suggestions are most welcome ....
I ALWAYS pull the refer when this type problem happens. I also replace the 2 fans and the fan tstat. The odds are the fans are ready to fail. I also always run a 2 wire harness from EACH side of the fan tstat wires down the backside and leave open. That way, in the future, it is easy to check the operation of the fan tstat and IF defective, you just jump those 2 wires and that activates the fans. Extra fans are NOT needed on a roof top vent system on a 1200 series. Does not hurt, but not really needed. Doug