ashlatz wrote:
Ok came home and ran the code. It's code #27
What should I do next? Thanks for the help
I assume you have a gasoline model. FC27 is no AC output voltage. Almost all Onans shutdown when no AC is produced. Here's the official troubleshooting guide, but basically, you check to see if you've got AC, and if not, you figure out why not. I still don't quite understand what the breaker has to do with this unless you've got an overload caused by a short. You'll notice that "Genset load" is actually the first listed possible cause below. We're back to one of the first things we discussed - verifying that the gen is producing AC. Turn off the breaker, start the gen and measure voltage between the breaker hot and gen neutral. It should be around 120 VAC.
VOLTAGE SENSE LOST – FAULT CODE 27
WARNING Some genset service procedures present hazards that can result in severe personal injury
or death. Only trained and experienced persons with knowledge of fuels, electricity, and machinery
hazards should perform genset service. See Safety Precautions.
Logic: No Sense Voltage (0 VAC across S1–S2) for 1 continuous second after start disconnect
Possible Causes: Genset loads, Inverter/Charger, VAC sense transformer, engine governor function, fuel
supply, choke, demand regulator, carburetor, generator windings, ignition, wire connections, temperature
Diagnosis & Repair:
1. Verify that Last Fault is FC 27: Yes, continue diagnosis; No, troubleshoot actual last fault.
2. Measure AC voltage.
3. Determine battery charge rate (typical default is 80 percent): if adjustable reduce to 30 percent.
4. Disconnect genset control P1 connector, verify P1 pins are fully inserted and inspect pin condition per
PSB–676: insert, repair or replace pins as necessary.
5. Reconnect P1 connector and test run genset for fault occurrence: repair or replace pins in connector as
necessary.
6. Check air filter cleanliness; replace air filter as necessary.
7. Check for blocked or damaged exhaust system: repair or replace exhaust components as necessary.
8. If the genset will not stay running measure genset frequency, quadrature winding and main winding voltages
using Break-Out Tool 420–0603 and Instruction Sheet R1098.
9. Gasoline Models
A. Under high ambient conditions or heat soak conditions vapor lock may occur, operate less than
120°F; verify proper installation to prevent air recirculation; correct as necessary.
B. Verify steady DC voltage at fuel pump while genset is running; repair wiring, verify proper installation
to prevent air recirculation as necessary.
C. Run genset on shop fuel supply; verify tank level and fuel line condition in vehicle.
D. Verify carburetor altitude setting; readjust as necessary.
E. Verify choke operation, setting and linkage damage; readjust, repair or replace as necessary.
F. Measure throttle stop frequency; readjust as necessary.
G. Measure fuel pump pressure/flow: replace fuel filter or pump as necessary.