The GFCI OUTLET itself is not current sensitive as far as "Total Anps" is concerned
IT IS. however very sensitive as to amps in v/s amps out. Even a couple mA (1/1000th) of an amp) will trip it if there is any imbalance in the hot and neutral currents.
IN short. your cooktop is the problem. Likely a very tiny hot to case short.
Now a GFCI Circuit breaker (Combination curcuit breaker and GFCI. will trip on overload as well as imbalance.
IT IS. however very sensitive as to amps in v/s amps out. Even a couple mA (1/1000th) of an amp) will trip it if there is any imbalance in the hot and neutral currents.
IN short. your cooktop is the problem. Likely a very tiny hot to case short.
Now a GFCI Circuit breaker (Combination curcuit breaker and GFCI. will trip on overload as well as imbalance.