PD4655 Charging Graph

I have been reading quite a bit about different converters and charge rates, specifically some claims that PD's seem to drop off earlier than other brands. That is not what I have noticed on my setup, so I figured I would test mine from 50% SOC and take some notes.

The batteries are a pair of Lifeline AGM GPL-6CT 300AH 6V's, which where new this spring.

The converter is a Progressive Dynamics PD4655 that was new in 2013.

I got the batteries drained down to an approx 50% SOC (12.21V after sitting disconnected for ~1 hour).

I was plugged into a 30A RV circuit on my house, with an input AC voltage of 118.2±0.5V thru-out the test.

I took readings every 1 minute for the first 15 minutes, then every 5 for the first hour, then every 15 thru 3 hours, and finally 30 minute readings until 5.5 hours.

The voltage at the converter was taken where the leads are soldered into the board with a handheld fluke.

The battery voltage was taken by the lead that feeds my Blue Sea voltmeter off of the distribution panel. I want to rewire the sample location to the lug on the battery box, but I haven't yet. It's less than 3' of wire from the box to the distro panel.

My ammeter is also a Blue Sea model.

I feel there is adequate wiring, the converter came with 10ga leads soldered to the board which are approx 10" long. From the board the positive side has ~18" of 6ga to the battery switch, then approx 18" of 2ga to the batteries. The negative side also has ~18" of 6ga to the neg bus bar, then ~10" of 6ga to the shunt, and then ~18" of 2ga to the batteries. The batteries are connected with a 6" section of 1ga.

I stated the test and began recording data. I didn't realize it for the first 6 minutes but the converter was not in "boost" mode. I gained around 0.6A by going into boost mode. I was current limited at that point still so the difference didn't amount to much in the total charge time.

I don't have a way to calculate amp hours in/out of the batteries but I did a linear calculation based on the amp hours. So over a 15 minute sample if the starting charge rate was 38.6A and the ending charge rate was 32.5A the average was 35.55A meaning that approx 8.9A where put into the batteries over that 15 minutes. It's not the most accurate, but better than nothing and probably pretty close. I used that to estimate the SOC, key word is estimate.

This first graph is the voltages and current. As you can see it holds a constant 56.4A for the first 15 minutes, but then only tapers down to 54.7A on the sample just before the converter voltage hitting the 14.47 set point at 90 minutes (the measured set point for my specific PD4655).



This graph shows the charge rate versus estimated SOC. You will noticed that the estimated SOC goes above 100%, this is based on my calculated SOC.



This is the sample data.



I am estimating 50-90 time at 2.5 hours.

I didn't include the data from the 10 hour mark, but at 10 hours the voltage was 13.75 and current had dropped to 1.4A. According to Lifeline the batteries are fully charged when the current drops below 0.5A per 100AH, or 1.5A for these. On long camping trips a 10 hour generator run every few charges will be required.


Based on the large capacity of the batteries the PD held full amperage for quite a while, but even on smaller or non-AGM batteries I feel it would have held full amperage until the voltage on the circuit board was 14.47. This is where wiring is crucial.

52 Replies

  • Nice job! Your PD is holding regulation for about 105 min. That's the best I've seen. Perhaps PD fixed their problems? Perhaps not.

    Bottom line, it's all about resistance. The lower the resistance, the more likely the PD will perform. There's a couple of reasons your charge looks good.

    1. You have AGM batteries. Battery resistance is half that of typical LA battery. Perhaps 10 mohm lower.

    2. You have low line resistance of about 0.4V/55A = 7.3 mohm. That's really low! Your typical cabling could have over 20 mohm resistance.

    A typical install has at least 10 mohm more resistance. At 55A, this increase in resistance raises the converter output voltage by: 55A * 10 mohm = 0.55V. After 6 minutes of charging, the PD will now operate at 13.49V + 0.55V = 14.04V. Other PD's couldn't hold regulation at that voltage.

    How industrious do you feel? Can you add 10 mohm more line resistance and repeat test? That should verify PD fixed the constant current mode of operation.
  • Excellent work!

    The thing that stands out most IMO is the "marker" for when to stop the gen at 90%. With Wets I find that to be at near 5 amps per 110AH of bank at 14.5v so for 300AH that would be when amps have tapered to 13.6a

    Here we see with 300AH of AGM (Lifeline type) 90% is reached at 30a or 10a per 100. So you could stop the gen sooner.

    My ugly graph with Wets shows a 50-90 on 300AH with 55amps would take 190 minutes. (300/220 x 139) The AGMs above took 150 minutes.

    Since both bulks are the same at 55a, the time saving with the AGMs has to be in a faster Absorption Stage at the same 14.4 voltage indicating a higher acceptance rate with AGMs during absorption.

    Perhaps the AGM guys can confirm/deny/elaborate on that aspect. I don't know AGMs well.

    Another consequence of that if correct, is you can get a shorter gen time by switching to AGMs instead of going to a higher amp charger with Wets. Could mean no fatter wiring either where you don't change the charger.

    With the OP info, it would be possible to estimate just how much time you could save either way and decide what each way would cost in dollars to change to that.