Your 75 amps on 225AH will look a lot like this graph at 70.
You are starting at 12.38 which is 70% SOC as mentioned. So if the charger is set to 14.6 and doing 75 amps, you are already past the Bulk stage and amps will be tapering from the start.

I am not sure if the voltage will stay at 14.6 for the 30 minutes in "three-stage mode" even if you are already past the Bulk stage, but i think so. It will then drop to 13.6.
If you are in single stage at 14.6 it will stay at 14.6 the whole way, which is what you want until the batts are full (as seen by an hydrometer reading) Then you can adjust back to 13.6 manually for the float stage. Or leave it at 14.6 and you can safely move the other switch to the left for 3-stage and it will do 13.6. See para 10.
I suspect you may have put the unit in three-stage and then turned the pot. Big no-no. That screws up all three voltages in the 3-stage mode. You can fix that by starting over in single stage, set 14.6 and now switch to 3-stage like it says in para 10
You should have set it to 14.8 anyway since these are Trojans. :)