I need to install a 30a RV outlet on the side of our house for our trailer. I need to go about 60 feet from the panel. Would 10/2 Romex be sufficient, or should I go bigger?
  • enblethen wrote:
    Number eight should work OK.
    I would suggest getting a digital plug in volt meter to keep an eye on voltage. Using air conditioning along with microwave could drop voltage down to minimum levels.
    I would check voltage at the panel where you are connecting new circuit. make sure it is in the 120+ range. If much below 120, you should think about the #6 wire.
    /\This... or just do it once, labor is expensive, and just buy and pull 6 gauge copper. Not worth the risk of voltage drop on expensive equipment like A/Cs or microwaves. Low voltage kills them quickly.
  • Number eight should work OK.
  • Ron3rd's avatar
    Ron3rd
    Explorer III
    gbopp wrote:
    You may want to Google a Voltage Drop Calculator. I just checked one and it recommended #6 wire for 30 amps @100 feet.
    #6 wire is the minimum.
    OK, so if I only need to go 60 ft, can I use #8?
  • You may want to Google a Voltage Drop Calculator. I just checked one and it recommended #6 wire for 30 amps @100 feet.