Vulcan Rider wrote:BB_TX wrote:
The 50 amp breaker is truly two separate hot legs with 50 amp capability each.
If that is true, why is it not called 100 amp service ?
Because you could pull (near to) 100 amps without overloading it, right ??
Given this, however, the answer to the original question would be:
The campground breaker is defective or is wired wrong and feeding more than one outlet.
It's 50 amp 240 volt service. With a a true 240 volt load, don't think you'll find anything like that in an RV, the max is 50 amps at 240 volts. When the load is multiple 120 volts loads then each hot leg can handle 50 amps. So yes it's 100 amps at 120 volts or 50 amps at 240 volts.